Generator teeny-tiny wires

Status
Not open for further replies.
I understand that a UL listed generator has been tested and approved as designed and that we need not question wiring practices we see in that equipment but holy smokes.....I just connected a 20 kW residential generator package which has a published maximum load current of 83 amps and which is fitted with a 100 amp circuit breaker and the wires between the generator and that breaker can't be bigger than #10! I know about temperature rating and all that but something just doesn't compute here for me. Can someone explain to me what I am missing?
 

iwire

Moderator
Staff member
Location
Massachusetts
You are not missing anything, it is all about temperature and the factory is counting on running those wires hotter than we could. They also must assume the voltage drop on such a short run is not an issue.
 

the blur

Senior Member
Location
cyberspace
I've seen similar situations, and the internal machine wiring melts after a few years. Keeps them in business.

I'm rebuilding a 1800 watt heating machine rated at 120volts. It's a custom production machine, and all the internal wiring melted....... why, because 1800 watts is pushing the limit for a standard cord and plug in a regular outlet... just stupid. it should have been a 240v machine.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
You are not missing anything, it is all about temperature and the factory is counting on running those wires hotter than we could. They also must assume the voltage drop on such a short run is not an issue.

You should see the wire sizes used on aircraft. They have to use teflon insulation because they run them very hot to save on weight.
 