pool receptacle

Status
Not open for further replies.

jhselectric

Member
Location
south jersey
I have a 50amp feed to a sub panel for a pool. The feed is in pipe and all the branch circuits for the pool are in seal tight. Can I come out of this panel with UF to feed the receptacle that is required 6-20 feet from pool?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The receptacle required by 680.22(A)(3) is not required to be run in a wiring method complying with 680.21(A) or 680.22(F).

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Chris,
Two questions, please.
(a) 680.22 (F) ?? What Code cycle. I can't locate it.
(b) Would the requirements of 680.21(A) apply to the "general purpose" receptacle. I see that for the pump receptacle but not the general purpose one.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Chris,
Two questions, please.
(a) 680.22 (F) ?? What Code cycle. I can't locate it.

Oop's I meant 680.23 (F) for wiring methods for underwater luminaires.

(b) Would the requirements of 680.21(A) apply to the "general purpose" receptacle. I see that for the pump receptacle but not the general purpose one.

I do not see 680.21(A) applying to the general purpose receptacles as 680.21 us titled "Motors". The requirement for the general purpose receptacle is located in 680.22 and there is nothing in 680.22 that would require a specific wiring method for the general purpose receptacles.

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
we are in agreement. I misread your post #2 (missed the "not".. DUH! )
 