richwaskowitz
Senior Member
- Location
- Shelby Twp. MI, near Detroit
I am preparing to connect a Generac 20 kW residential unit. Since the breaker in the genny is rated at 100 amps, I planned on running 3 AWG THWN hot and neutral wires (100 amps at 75 degrees C per table 310.16). The lugs on the breaker are fine BUT, the neutral terminal in the genny only accepts up to a #6! Now I am not even clear on what wire ampacity I am required to run for either the neutral or the hots.