What does code say about using #3 awg copper for the hots, #3 awg copper for neutral and # 8 awg copper for ground on a 135 ft run between the main and this 100 amp subpanel?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What does code say about using #3 awg copper for the hots, #3 awg copper for neutral and # 8 awg copper for ground on a 135 ft run between the main and this 100 amp subpanel?

With 75? C terminations the NEC says that your installation is code compliant. Is someone saying otherwise?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I will note that, although it is not a NEC violation, at 50 amps or greater you will be exceeding the recommended voltage drop with a #3.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
What does code say about using #3 awg copper for the hots, #3 awg copper for neutral and # 8 awg copper for ground on a 135 ft run between the main and this 100 amp subpanel?

can't say there is anything "wrong" with it code wise.

might have VD issues at high usage times.

presumably you have done a load calculation and this installation is adequate to support that.

is the main 100A as well?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I will note that, although it is not a NEC violation, at 50 amps or greater you will be exceeding the recommended voltage drop with a #3.
That would be the case assuming a 100% unbalanced load. With a balanced load and or line to line loads the current can go up will out exceeding the voltage drop recommendations.
 

hardworker

Senior Member
The main is a 200amp panel. The building owner was worried about voltage drop on the 135 run. The 100amp sub will never pull more than 70amp.
 