jeff48356

Senior Member
In a detached garage, would a sub-panel be required to have its own ground rod driven into the ground next to the garage? If so, what is the reasoning for this? How would a sub-panel in a garage be different from any other sub-panel in the house? The one in the garage is fed with four conductors (black, red, white, ground).
 

Howard Burger

Senior Member
two rods or ufer

two rods or ufer

You'll also find a relatively recent post on this forum discussing this question, and that two ground rods are needed (or a ufer if you can get in when the foundation is poured).
 

ACE1970

Member
Location
California
for the cleveland apprentice

for the cleveland apprentice

do some reading art.250.32a each building or structure requires a GES 250.32b1 neutral must be isolated to prevent a fault going upstream to main panel so thar the GES takes a fault directly to ground.
 
Last edited by a moderator:

Volta

Senior Member
Location
Columbus, Ohio
do some reading art.250.32a each building or structure requires a GES 250.32b1 neutral must be isolated to prevent a fault going upstream to main panel so thar the GES takes a fault directly to ground.

You probably mean so the GES can help direct lightning hit energies more directly to ground, don't you? And that it helps to stabilize to system voltage to the local ground potential?
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician

AK GUY

Member
Location
juneau, AK. USA
Did you run an equipment grounding conductor with the feeders to the garage? If so drive a ground rod and isolate the grounded conductor from the grounding conductor. If not drive a ground rod and bond the grounded conductor terminal to the grounding electrode conductor. Also the garage is required to have a main disconnect.
 