FEEDER????
Alwayslearningelec
NJ
Estimator
When the word feeder is mentioned I know that to usually mean the wire and conduit but isn't a feeder just the wire? THanks.
iwire
Massachusetts
Feeder. All circuit conductors between the service equipment,
the source of a separately derived system, or other
power supply source and the final branch-circuit overcurrent
device.
Beyond that I think it will be local terminology.
infinity
New Jersey
Journeyman Electrician
Look at Bob's definition. The important parts are the locations of the OCPD, this is what differentiates it from a branch circuit.
charlie b
Lockport, IL
Retired Electrical Engineer
I can see your reasoning, it is not necessary for the circuit to function, correct?
That is how I see it too. The ungrounded and grounded conductors comprise the feeder, but not the raceway, and not the EGC. That said, I will list the EGC in the table I put on the drawings to describe various feeder types. This is one of the situations in which the common, conversational use of a word is different from the precise definition of the word.
iwire
Massachusetts
That and these:)
Grounded Conductor. A system or circuit conductor that
is intentionally grounded.
Grounding Conductor, Equipment (EGC). The conductive
path installed to connect normally non?currentcarrying
metal parts of equipment together and to the system
grounded conductor or to the grounding electrode
conductor, or both.