Another coordination question I have been pondering:
If I have a bus and feeding this bus is two identical transformers fed from different sources what is typically required for coordination of the breakers on this bus.
Lets say that on the secondary of each transformer there is a breaker which is connected to the bus and feeding power to the bus. Then tapped off of the bus there are several feeder breakers.
Do you simply need to coordinate each of the transformer secondary breakers with the largest feeder breaker on the bus?
Do you need to account for both transformers operating as well as only one transformer operating? For both transfoerms operating is there anyting special reqired to account for only portion of feeder fault current (1/2) being seen by each transformer secondary breaker?