Multi Wire Branc Circuits..
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
This is what Al is talking about.
ry%3D480
gndrod
Ca and Wa
Safety concern
Safety concern
Great diagram Dennis.
NEC 210.7 still requires a common handle tie for the MWBC simultaneous trip for this wiring configuration. This becomes a safety issue in instances where one branch circuit causes a blackout situation by tripping another circuit that cannot be reset immediately. The NEC needs to address this by stating how one branch circuit must not affect another critical circuit such as lighting or medical equipment using a shared neutral. I believe this is another good reason to restrict MWBC wiring in certain facility or dwelling conditions.
al hildenbrand
Minnesota
Electrical Contractor, Electrical Consultant, Electrical Engineer
Great diagram Dennis. NEC 210.7 still requires a common handle tie for the MWBC simultaneous trip for this wiring configuration.
Look at that language of 210.7, again. It says "simultaneous disconnect", not "common trip"A fused two or three pole safety switch is a simultaneous disconnect, like a handle tie.
gndrod
Ca and Wa
perfection
perfection
Thank you Jack and Al for keeping me on the straight and narrow to my lax use of the word 'trip' in lieu of "Simultaneous disconnect" as NEC language for two phase legs of a MWBC.
Whether both legs disconnect depends on the brand and type of a two pole configuration. On breaker ties, one 'tripped' handle may have a loose enough tie so as not to disconnect both circuits. A single handle double pole breaker would have been a more appropriate reference.
Lighting Circuits as MWBC
Although the 2011 code is prohibiting MWBC it has been used in commercial fields for years. IE 277V lighting circuits have traditionally be three hots a neutral w/ ground.
I think this becomes a matter of what code is being currently enforced as I have been in municipalities where the AHJ were using 2004 NEC as enforced standard in 2011.
Have a good day a a great holiday regardless - remember be safe out there we work with the invisible that is not afraid to reach out and touch us.
Steve
hurk27
Steve
It doesn't prohibit MWBC's it just makes it clear that you cant place them on the same phase and run a larger neutral that it didn't prohibit in the past.