Grounding and Bonding

Status
Not open for further replies.

Hopewell

Member
Location
South Bend,In
What is the minimum size conductor that is permissible to be used as a bonding conductor from a half inch diameter ground rod to flare stack (used to burn ?off/ incinerate off gases) that is 30 feet long by 2 feet in diameter?
Are conduit beam clamp permissible to be used as bonding clamp?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Are you asking about an auxiliary ground rod?

Roger
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
What is the minimum size conductor that is permissible to be used as a bonding conductor from a half inch diameter ground rod to flare stack (used to burn –off/ incinerate off gases) that is 30 feet long by 2 feet in diameter?
Are conduit beam clamp permissible to be used as bonding clamp?

I don't know that there is actually any requirement to do this at all. Therefore, there are probably no conductor sizing rules at issue.

generally beam clamps are not listed to be used as ground clamps, but given as this is not a required connection, one might well argue that it is a clothes line and there are no requirements in the electrical code for how clothes lines are installed.
 