Where is it required in the NEC that Rigid metal conduit have a locknut on the inside and outside of the enclosure. I know it is required, but I can?t find it in the white book or the NEC
The only place in the NEC where if specifically states this is 250.97(2) for voltages over 250, and a few places in article 550, but how else are you to secure RMC to a box?
The only place in the NEC where if specifically states this is 250.97(2) for voltages over 250, and a few places in article 550, but how else are you to secure RMC to a box?
Where is it required in the NEC that Rigid metal conduit have a locknut on the inside and outside of the enclosure. I know it is required, but I can’t find it in the white book or the NEC
A wholly metal bushing and one locknut is permitted if the conductors are #6 and smaller. #4 and larger would require a bushing that is insulated.
300.4(G) Insulated Fittings. Where raceways contain 4 AWG or larger insulated circuit conductors, and these conductors enter a cabinet, a box, an enclosure, or a raceway, the conductors shall be protected by an identified fitting providing a smoothly rounded insulating surface, unless the conductors are separated from the fitting or raceway by identified insulating material that is securely fastened in place.
Exception: Where threaded hubs or bosses that are an integral part of a cabinet, box, enclosure, or raceway provide a smoothly rounded or flared entry for conductors.
Conduit bushings constructed wholly of insulating material shall not be used to secure a fitting or raceway. The insulating fitting or insulating material shall have a temperature rating not less than the insulation temperature rating of the installed conductors.
The only place in the NEC where if specifically states this is 250.97(2) for voltages over 250, and a few places in article 550, but how else are you to secure RMC to a box?
So, by reading these posts i understand that RMC connecting to a box or cabinet doesn't require (2) locknuts? one inside and one outside????
How will the conduit be secured to the box?
am i understanding this correctly? so if i install one locknut on the inside of the box it is OK?
So, by reading these posts i understand that RMC connecting to a box or cabinet doesn't require (2) locknuts? one inside and one outside????
How will the conduit be secured to the box?
am i understanding this correctly? so if i install one locknut on the inside of the box it is OK?
You might want to look at the various hazardous location applications mentioned where "... locknut-bushing and double-locknut types of contacts shall not be depended on for bonding purposes, but bonding jumpers with proper fittings or other approved means of bonding shall be used." [Underline mine] Obviously it doesn't prohibit it, but you need to be prepared for a much more rigorus bonding method....
501.30(A), 502.30(A), 503.30(A), 505.25(A) & 506.25(A) refers to "locknut-bushing" and "double locknut" methods...
You might want to look at the various hazardous location applications mentioned where "... locknut-bushing and double-locknut types of contacts shall not be depended on for bonding purposes, but bonding jumpers with proper fittings or other approved means of bonding shall be used." [Underline mine] Obviously it doesn't prohibit it, but you need to be prepared for a much more rigorus bonding method.
.... Remember, if you follow the NEC to the letter you will be no more than the worst electrician allowed by law.
To secure RMC to a box with one locknut, the locknut wouls have to be on the outside and a metal bushing on the inside.
The locknut on the outside would have to be tightend after the metal bushing is screwed on the end of the RMC so there is contact between the box, bushing and locknut.
I agree that there may be additional bonding required for hazardous locations, but I was just trying to point out that for systems under 250 volt to ground, the single locknut-bushing method is not prohibited by code and acceptable for bonding purposes for RMC and IMC.
that's excellent