Lights flicker

Status
Not open for further replies.

bwyllie

Senior Member
Location
MA
On a projects where there are (3) xfmrs off of one distribution boards, the lights powered from only one of the transformers will flicker for periods of time, typically when restaraunt is full. any suggestions or experiences with such problems? Contractor has verified the correct dimmer and ballast configurations.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Might that panel also feed largish motor loads, like the walk in freezer or the AC that come on and off automatically, making it random? If the system is sized marginally or poorly balanced, motor starting can make the lights flicker.
 

hurk27

Senior Member
I would lean toward a mis application between the ballast and dimmer, removing the dimmer and using a regular switch to just see if the flicker is still there, in cases like this a fluorescent lamp will more strobe then just flicker if that is what it is doing.
 

robbietan

Senior Member
Location
Antipolo City
I once saw a place where the transformer is 98% loaded, the lights would flicker every time the 15HP water pump would kick in. and then the UPS would ring alarm bells. and then the people would go crazy
 