250.24(B) Main Bonding Jumper. For a grounded system, an
unspliced main bonding jumper shall be used to connect the
equipment grounding conductor(s) and the servicedisconnect
enclosure to the grounded conductor within the
enclosure for each service disconnect in accordance with
250.28.
Not sure if you can:
Sounds like it must be "within" the service disconnect?
250.24 Grounding Service-Supplied Alternating-Current
Systems.
(A) System Grounding Connections. A premises wiring
system supplied by a grounded ac service shall have a
grounding electrode conductor connected to the grounded
service conductor, at each service, in accordance with
250.24(A)(1) through (A)(5).
(1) General. The grounding electrode conductor connection
shall be made at any accessible point from the load end
of the service drop or service lateral to and including the
terminal or bus to which the grounded service conductor is
connected at the service disconnecting means.
(B) Main Bonding Jumper. For a grounded system, an unspliced
main bonding jumper shall be used to connect the
equipment grounding conductor(s) and the service-disconnect
enclosure to the grounded conductor within the enclosure for
each service disconnect in accordance with 250.28.
Exception No. 1: Where more than one service disconnecting
means is located in an assembly listed for use as service
equipment, an unspliced main bonding jumper shall
bond the grounded conductor(s) to the assembly enclosure.
Exception No. 2: Impedance grounded neutral systems
shall be permitted to be connected as provided in 250.36
and 250.186.
250.142 Use of Grounded Circuit Conductor for
Grounding Equipment.
(A) Supply-Side Equipment. A grounded circuit conductor
shall be permitted to ground non–current-carrying metal
parts of equipment, raceways, and other enclosures at any
of the following locations:
(1) On the supply side or within the enclosure of the ac
service-disconnecting means
(2) On the supply side or within the enclosure of the main
disconnecting means for separate buildings as provided
in 250.32(B)
(3) On the supply side or within the enclosure of the main
disconnecting means or overcurrent devices of a separately
derived system where permitted by 250.30(A)(1)
I again agree with Hurk,
Boy your in a agreeable mood tonite:lol:
kinda scary, isn't it ?