I'm going to wire a new hot tub,240 volt/50 amp 2 wire and ground.The book says to bond the interior to a ground rod using #8 awg. I will to cover warranty issues,but is this code?
I'm going to wire a new hot tub,240 volt/50 amp 2 wire and ground.The book says to bond the interior to a ground rod using #8 awg. I will to cover warranty issues,but is this code?
It is code in the sense that we must follow manufacturers instructions. Probably the reason for the ground rod is to protect their electronics from lightning or surges. That is the only reason I can think of for that requirement.I'm going to wire a new hot tub,240 volt/50 amp 2 wire and ground.The book says to bond the interior to a ground rod using #8 awg. I will to cover warranty issues,but is this code?
It is code in the sense that we must follow manufacturers instructions. Probably the reason for the ground rod is to protect their electronics from lightning or surges. That is the only reason I can think of for that requirement.
Well I cannot think of any other reason for a ground rod, can you?Hopefully the equipment has a built in surge arrestor that shunts the surge to ground otherwise that reason does not have much validity IMO.
Well I cannot think of any other reason for a ground rod, can you?
Well I cannot think of any other reason for a ground rod, can you?
Uneducated people writing requirements, just like the 6 AWG EGC some hot tub makers require.
No doubt yet UL stamps it based on what the company writes. I can get a UL approval equipment and state anything I want. It's like the hydromassage tub manufacturer that req. a #8 back to the panel for bonding. It's is total BS but we have to abide by it since the manufacturer wrote it even if written by an uneducated individual. Why are they writing the manuals????Uneducated people writing requirements, just like the 6 AWG EGC some hot tub makers require.
No doubt yet UL stamps it based on what the company writes. I can get a UL approval equipment and state anything I want.
It's like the hydromassage tub manufacturer that req. a #8 back to the panel for bonding. It's is total BS but we have to abide by it since the manufacturer wrote it even if written by an uneducated individual. Why are they writing the manuals????
No, I think it is spot on. At least that is my take-- CYA seems to be their MO, even with meaningless dribble.Of course the above is a total guess and could be entirely wrong.
It is too bad that we can't have a boycott of these companies. Basically telling the ho's that certain companies are costing you needless amounts of money on the install. It seems like it is just a few companies and not the majority.
The does not say that. It says"It is code in the sense that we must follow manufacturers instructions. Probably the reason for the ground rod is to protect their electronics from lightning or surges. That is the only reason I can think of for that requirement.
Manufactures instructions are not really part of the listing and labeling. As far as I am concerned, if the requirement is not in the actual listing standard or the White Book, it is not a 110.3(B) instruction. I know that UL says otherwise, but I don't agree, and I will never agree as long as UL continues to "classify" breakers.(B) Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
The does not say that. It says"
Manufactures instructions are not really part of the listing and labeling. As far as I am concerned, if the requirement is not in the actual listing standard or the White Book, it is not a 110.3(B) instruction. I know that UL says otherwise, but I don't agree, and I will never agree as long as UL continues to "classify" breakers.
That is speaking to how I read the code. That does not mean that I would ignore a manufacturer's "recommendation" on an installation. I would have to comply with the recommendation to protect myself from civil suits in the event of a malfunction of the equipment.
Yes, I am well aware of what UL says, but until they stop classifying breakers I will continue to say that the only listing and labeling instructions are those found in the standard itself or in the White Book. They cannot have it both ways, but that is exactly what they are telling me when they says all of the instructions provided are 110.3(B) instructions and then they turn around as say when some one pays them money to classify a device for use in violation of the original equipment manufacturer's instructions that is ok.Don, I have talked with UL and they insist that their instructions are part of the listing and labeling. Maybe you know someone higher up the food chain but that is what I am told.