You have to? You HAVE to??? Where exactly within 220 does it say you have to go to 210? :happyno:
Try this one: The NEC is not a design manual. :happyno:
I agree, the NEC is "not intended as a design specification or an instruction manual for untrained persons." It is however, a manual that "Compliance therewith and proper maintenance results in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use." In other words, I believe it is the minimum allowed if enacted. "The NEC is not a ceiling to reach for, but rather a floor to work up from." (I wish I could remember where I first heard that...)
90.3 is an excellent place to start. "Chapters 1, 2, 3, and 4 apply generally;" from there we can move to 90.5(A)(Shall).
Now on to my statement:
In a bank or office building, if I have 2401 sq ft, I have to install two circuits versus installing 14 receptacles(or 13 doubles and one single) from 220.14(K)(2). From there I have to go to 210.11(B) for distribution
.
Because I have calculated this load based on sq.ft., I am not refered back to 210.11, but I must remember to apply 210.11.
210.11(B) states in part, "This load shall be evenly proportioned among multioutlet branch circuits within the panelboard(s). 90.3 states the chapters apply generally, I take that to mean that I must use any parts in chapters 1,2,3,& 4 that pertain to my specific installation.
220 does make a couple of references to 210.11. 220.14(I) & 220.14(J)(1).
Should the NEC always refer the reader back to specific articles? Or should the person utilizing the NEC be expected to be familiar with the book before use.
I see this like any good book, if you are going to follow the story line, it is important to know the first few chapters.