Can the circuit breaker supplying a 112.5kVA, 480-208/120 transformer be considered the disconnecting means per 450.14 if I install a permanent lock hasp on the breaker? It will not be within sight of the transformer.
450.14 Disconnecting Means.
Transformers, other thanClass 2 or Class 3 transformers, shall have a disconnectingmeans located either in sight of the transformer or ina remote location. Where located in a remote location,the disconnecting means shall be lockable, and the location
shall be field marked on the transformer