Transformer Primary Disconnecting Means

Status
Not open for further replies.

sii

Senior Member
Location
Nebraska
Can the circuit breaker supplying a 112.5kVA, 480-208/120 transformer be considered the disconnecting means per 450.14 if I install a permanent lock hasp on the breaker? It will not be within sight of the transformer.

450.14 Disconnecting Means.​
Transformers, other thanClass 2 or Class 3 transformers, shall have a disconnectingmeans located either in sight of the transformer or ina remote location. Where located in a remote location,the disconnecting means shall be lockable, and the location
shall be field marked on the transformer
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
to cover another "base".... are they both in the same building ?
 