Wall Mounted AC demand factors for Hotel (125 rooms)

Status
Not open for further replies.

nmartz

New member
Location
Chico, CA, 95928
I'm new to the forum and was wondering if you guys know what factor to apply to wall mounted AC units for a hotel. I have been looking through the tables in NEC section 220 and have not really found one that exactly fits this situation. Each wall mounted AC unit would draw 6.6 Amps cooling and 8.9 Amps heating. I appreciate the help.
 

kbsparky

Senior Member
Location
Delmarva, USA
You don't want to apply any demand factors less than 100% to those units.

It appears that your heating load is greater than the cooling load?
 
Status