Odd situation question. Current project has an old 60A 120/240V 1-phase service. load consists of a couple lights and a larger motor across the line start. The project is to incorporate an emergency generator to back up entire service. due to age of service, will be replacing with 100A service. When sizing the generator, due to the motor, the genrator is larger than the service (won't be installing a VFD). The generator breaker will be 150A-2P hence a 150A rated transfer switch. However, the service disconnect will be 100A fused, then the 150A transfer switch, and then a single panel on transfer switch output with a 100A main breaker. Never had a situation where the running load is so small yet the motor inrush requires a large genset.
So, should the service and panel be changed to 150A to keep the system common per say? Or is a 100A service with a 150A rated genset and 150A transfer switch ok? Anybody run into this before? I just can't see a 150A service for such a small load. Heck, the peak utility demand over the past year has only been about 9Kw. Maybe I should make everything 150A rated and be done with it.
thanks.
So, should the service and panel be changed to 150A to keep the system common per say? Or is a 100A service with a 150A rated genset and 150A transfer switch ok? Anybody run into this before? I just can't see a 150A service for such a small load. Heck, the peak utility demand over the past year has only been about 9Kw. Maybe I should make everything 150A rated and be done with it.
thanks.