Application: Existing 200-amp single-phase 240V service. Customer wants to add a transfer switch for a future generator and move the panel to the middle of the house on the 1st floor.
I plan on adding a 200 amp, service rated, N3R, manual transfer switch next to the meter pan, As I read 230.91, I must also add OCP next to the transfer switch as opposed to using a sub panel with a 200 amp main. If I am wrong, let me know.
My question is this, same scenario but the sub panel would be just below the transfer switch, and located in the basement. If I read 230.91 correctly, I still need OCP adjacent to the transfer switch. I do not view the basement sub panel location as adjacent, but if I had no transfer switch, the OCP could be in the main panel, same location in the basement. Have I missed something or is this just the way it is?
:slaphead:
I plan on adding a 200 amp, service rated, N3R, manual transfer switch next to the meter pan, As I read 230.91, I must also add OCP next to the transfer switch as opposed to using a sub panel with a 200 amp main. If I am wrong, let me know.
My question is this, same scenario but the sub panel would be just below the transfer switch, and located in the basement. If I read 230.91 correctly, I still need OCP adjacent to the transfer switch. I do not view the basement sub panel location as adjacent, but if I had no transfer switch, the OCP could be in the main panel, same location in the basement. Have I missed something or is this just the way it is?