Step up transformer calculation

Status
Not open for further replies.

Nietz001

Member
Location
St Paul MN
I have an unusual request to step up power from 208 to 480volts. If anyone cares to help I will give you my answer and hopefully I'm correct.
208 3 phase to 480 volts 3 phase
load at secondary - 480 volts is 125 amps
My math tells me I need a 415kva transformer at 208 to get the power I need.
Does this sound right, that's a big transformer
 

jdcpe17

Member
Location
Austin, Texas
this isnt that unusual. kva rating would be the same looking at the primary or secondary. the volts and amps both change. now something else you could consider, the transformer can be basically 125% over used... meaning you could potentially go as low 83.14 kVA. but youre not going to find a 83 kva transformer... make sure you get wye and delta orientation correct for whatever you need...
 

templdl

Senior Member
Location
Wisconsin
Also, If I may suggest that you specify a 208 delta to a 480Y/277 transformer. It is not all that unusual for 208Y primary to be specified based upon the source voltage of 208Y/120 and a 480 delta 3w secondary based upon the neutral not being required but with little regard to just how you are going to ground it.
 

Nietz001

Member
Location
St Paul MN
I guess I knew that the transformer would be sized by the load at the secondary, I guess what I was thinking is what size would the primary need to be. Assuming the transfomer has a turns ratio of 4:1 wouldn't that be about 600 amps on the primary or am I mising something?
Jeff
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I guess I knew that the transformer would be sized by the load at the secondary, I guess what I was thinking is what size would the primary need to be. Assuming the transfomer has a turns ratio of 4:1 wouldn't that be about 600 amps on the primary or am I mising something?
Jeff

You are missing something...the turns ratio is 1:2.3. The primary current would be 288 Amps with a load current of 125 Amps.
 
Last edited:

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
I guess I knew that the transformer would be sized by the load at the secondary, I guess what I was thinking is what size would the primary need to be. Assuming the transfomer has a turns ratio of 4:1 wouldn't that be about 600 amps on the primary or am I mising something?
Jeff

KVA is KVA! it doesn't matter which side of the transformer you are on.

(sqrt 3) x 480V x 125A = 104kVA (load)

Standard size transformer will be 112.5KVA; at 208V that's 312A, at 480V that's 135A.
 