Conduit behind a control panel

Status
Not open for further replies.

AZElectrical

Member
Location
Arizona
I have a situation where wall space is needed to install a control panel for a jockey pump. The panel will be fed from a 15A3P 480V circuit breaker in a distribution board nearby. Due to the equipment layout in the room, the best place to put said control panel is on a wall that already has a conduit (1" GRC) installed on it. The conduit runs vertically on the wall and contains wiring for a 120V damper in nearby ductwork.

The question: Is it code compliant (2011 NEC) to mount the control panel on uni-strut, over top of the existing conduit on the wall? Would 110.26(E)(1)(a) rule this installation out? Is the uni-strut considered to be part of the depth of the equipment (control panel), and therefore the existing conduit is "foreign to the electrical installation?"
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
I would not consider the jockey pump controller to be a "switchboard, panelboard, or motor control center." Therefore, 110.26(E)(1)(a) would not apply to the installation of the controller.
 