Is the ground wire in NM smaller than the black and white wire? I know that years ago it was, but is that the case now? I am asking because this is mentioned in the FAQ in this NEC forum.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is the ground wire in NM smaller than the black and white wire? I know that years ago it was, but is that the case now? I am asking because this is mentioned in the FAQ in this NEC forum.
The egc is the same size as the conductors in sizes 14-10. Once you get higher then that the sizes change to match, hopefully with 250.122. This can be a problem when upsizing for VD as the EGC may not change depending on the wire sizes.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
MN in sizes 14, 12, and 10 has had a full sized EGC (in the NEC world) since the late 60's or very early 70's.
 