MCCB Instantaneous Trip Setting

Status
Not open for further replies.

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
In general, it must be set to trip below the minimum fault current that it will see, assuming the maximum capability of the equipment is greater than the minimum fault current.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Read Article 430, specifically table 430.52, and read the exceptions as well, and make sure you understand all of them. If you have more uestions after that, post them here again.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I think the poster is asking about a molded case circuit breaker.

If that is the case to determine the instantaneous trip threshold you need to get the circuit breakers trip curve data from the breaker manufacture.

Chris
 

zog

Senior Member
Location
Charlotte, NC
Does anybody know how to determine an MCCB instantaneous trip setting? I haven't done this in a couple years. I was thinking 10 or 15x the FLA?

Thanks.

Are you asking how to determine WHERE it should be set or how to determine WHAT it is set at?
 

ATSman

ATSman
Location
San Francisco Bay Area
Occupation
Electrical Engineer/ Electrical Testing & Controls
Does anybody know how to determine an MCCB instantaneous trip setting? I haven't done this in a couple years. I was thinking 10 or 15x the FLA?

Thanks.

To be compatible with the coordination study, it should be set at just above the inrush current of the largest connected load on startup. If the breaker is in an MCC then I would follow the old Westinghouse recommended procedure: 1. Raise the inst dial to max. 2. Start and stop the motor. 3. Lower the setting 1 notch each time you restart motor until the breaker trips, then raise the dial 1 notch. 4. Restart motor to prove no-trip. This will be the final setting. This setting should match the trip curves in the study and also takes into account cable impedance, as well.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
To be compatible with the coordination study, it should be set at just above the inrush current of the largest connected load on startup. If the breaker is in an MCC then I would follow the old Westinghouse recommended procedure: 1. Raise the inst dial to max. 2. Start and stop the motor. 3. Lower the setting 1 notch each time you restart motor until the breaker trips, then raise the dial 1 notch. 4. Restart motor to prove no-trip. This will be the final setting. This setting should match the trip curves in the study and also takes into account cable impedance, as well.

When doing this type of "click and hope" adjustments, make sure you are not exceeding both the # of starts/hr and the time between starts of the driven equipment.
 