is a 120 Volt receptacle installed in a garage for a washing required to be GFCI protected? I have looked at 210.8 but it doesn't address individual branch circuits.
is a 120 Volt receptacle installed in a garage for a washing required to be GFCI protected? I have looked at 210.8 but it doesn't address individual branch circuits.
That is new to me. It looks like they changed it in the 2008 code. That kind of stinks because now the receptacle for the garage door opener has to be a GFCI (Hopefully, you would install the reset at the breaker or a receptacle in the wall so it is easily reset).
Good info in this forum.
If you are on the 2011 you must install the gfci in a readily accessible location. We use a dead front GFCI by the door to the house, for the garage door opener.