Electrical Room/Closet with swinging doors to exterior

Status
Not open for further replies.

apelkner

Member
I know that your working space can overlap doors such as in a shallow electrical closet, but what if those doors lead to the exterior of a building? Should you try to keep your working space confined within the room (thinking about outdoor conditions like rain, storms, etc)? Is there a code reference?

Thanks.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Should you try to keep your working space confined within the room?
Should you? I should. Would it be a code violation if you don't? It would not. As to code references, try the second sentence of 90.1(B). :happyyes:
 