Multiple wires under breaker terminal

Status
Not open for further replies.

rich000

Senior Member
In a normal situation, I know this will not pass.

But, this is being used inside a piece of switchgear for the controls inside the switchgear.

I believe this is a UL vs. NEC thing. I just hate when the manufacturer's make something that violates the NEC.

IMG_2858.jpg
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Its impossible to tell from the photo, but the QCR breaker has on option for "quick connect terminals" which allows for the installation of two 10 AWG conductors with slip on terminals. That option may be installed in your case.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I agree, this is factory wiring so the NEC doesn't apply.
How do we know this came from a factory and it is not custom 'field' work?
I have seen several installations where a local installer didn't 'need no stinking instructions'.
 

cadpoint

Senior Member
Location
Durham, NC
It looks like low voltage work, larger wire just for distance alone and the dial/knob with it, probably a custom install since each breaker has it's own frame rail!

Correct and vibable well that's always subject to an inspection(,or in Forum fashion)!
:)
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
The wire markers hide the terminations too well to tell, but I have many clients who use ferrules at all terminations. There are 2:1 ferrules which I find used quite often.
 