voltage drop

Status
Not open for further replies.

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
You also need to tell us whether this is a single phase or three phase circuit. I know we don't often see three phase in residential units, but I still need to ask, rather than make an assumption.

Welcome to the forum.
 

jumper

Senior Member
are you paralleling the #12's???

Wouldn't that be illegal? 310.10(H)(1)

(H) Conductors in Parallel.
(1) General. Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded circuit
shall be permitted to be connected in parallel (electrically
joined at both ends) only in sizes 1/0 AWG and larger where
installed in accordance with 310.10(H)(2) through (H)(6).
 

Eng

Member
Wouldn't that be illegal? 310.10(H)(1)

(H) Conductors in Parallel.
(1) General. Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded circuit
shall be permitted to be connected in parallel (electrically
joined at both ends) only in sizes 1/0 AWG and larger where
installed in accordance with 310.10(H)(2) through (H)(6).

It was an attempt at humor based on the information provided. the only he can supply an 11KW load with #12 is if he uses multiple sets.
 