- Engineer
We are getting open delta 240/120 3ph. at a residence. The PoCo is feeding (1200 ft) a 25/10KV duplex transformer with two "1/0A EPC CONC ENC PE" runs from their 3ph 22KV P-P pole run.
A local HV contractor {& retired PoCo employee} stated there should a bare neutral run also, as depending on the concentric sheath for the current-carrying neutral is a bad idea. I've also been told that by others.
How common is this approach? Should I be concerned? In theory, when/if the cables fail, it's their problem...but my client would be burning propane for many days before ever they fixed such. And open neutrals worry me.
A local HV contractor {& retired PoCo employee} stated there should a bare neutral run also, as depending on the concentric sheath for the current-carrying neutral is a bad idea. I've also been told that by others.
How common is this approach? Should I be concerned? In theory, when/if the cables fail, it's their problem...but my client would be burning propane for many days before ever they fixed such. And open neutrals worry me.