bcarne
Member
- Location
- Omaha, NE, USA
I have an addition to a school that is finishing up construction. The new addition is fed from a 2000 amp 277/480v service and the existing building is fed from an 800 amp 120/208v service. I met the 230.2C1 stating that I can have two services is the services total more than 2000 amps. I kept the buildings and services separate with a fire door, but also bonded them together with a #3/0 per 250.58. An issue in part of the new construction came up where the school wanted a 400 amp service to their new performing arts area for lighting and sound. Seems kind of overkill to me, but the customer is always right. I didn't have room in the new 2000 amp service, but did from the existing school 800 amp service since that fed part of the school that was torn down.
Now the inspector is having an issue with the two services feeding this theater and wants a fire wall, fire doors, all of the existing 120v circuits rerouted to the new lighting and sound panel and a subfed 277v panel to fed the heat pumps and lighting in that area. My assumption was that I was ok to feed the area with both services since the services were bonded together per 250.58. Is the inspector right, or do I have a case to argue against him on this?
Now the inspector is having an issue with the two services feeding this theater and wants a fire wall, fire doors, all of the existing 120v circuits rerouted to the new lighting and sound panel and a subfed 277v panel to fed the heat pumps and lighting in that area. My assumption was that I was ok to feed the area with both services since the services were bonded together per 250.58. Is the inspector right, or do I have a case to argue against him on this?