Nightmare ArcFault OD...in the AHJ's daughter's house!!!

Status
Not open for further replies.
T

T.M.Haja Sahib

Guest
It changes the impedance of the circuit. It worked for us on that particular installation. Just something to try if all else fails. I was not there but my help looked for all the typical causes, switched AFCIs, etc. I then talked him thru the process of adding 25' of cable to the circuit. It worked. He settled for looping the hot a couple times around the interior of the panel. Seems there can be a "sweet spot" for AFCIs with the length of cable being a problem. I believe it was a CH tech note that pointed me to that fix.

Increase in circuit leads to increase in leakage current and so AFCI is liable to trip.Above it is stated 25' of cable was added to solve a AFCI tripping problem.Incomprehensible!
 

cowboyjwc

Moderator
Staff member
Location
Simi Valley, CA
When you say "tore" house apart, do you mean literally? You could have a nail in a wire or a staple in to tight. The breakers are just doing their job. Just checking at the connection points isn't really going to cut it.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Going back to the OP, your circuits should not open "at will". The only problems we have had with AFCIs are with particular loads, ie universal type motors and one older dorm type refig that used a klixon style thermostat.

Change your method of install. Meg circuits before the wall covering goes on. L-N, N-EG, & L-EG. Continuity checks will show a major screw up but you need more. Meg again after wall covering goes on.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I have really taken a liking to the plastic staples from Big Orange for that reason. I hated seeing them for a long time, too homeowner looking. But they do keep from pinching wire & are easier to drive in old seasoned lumber. Even if the nails bend, they still hold & don't damage wire. Someone would almost have to purposely drive it wrong to damage wire.

I'm in your camp on this, but I think we are alone on this. I think they have lots of advantages and one would think if they were sold in bulk like regular NM staples they might even be cheaper than staples. I think Ideal makes the ones I use.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
... The only problems we have had with AFCIs are with particular loads, ie universal type motors....
That is odd. I have tested AFCI's with universal motors and not had a problem. Big blue arc and the breaker did not trip.

The only problem I did have, that was not related to a problem with the circuit was new tools with a soft start feature. Two different brands of breakers.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I think the only thing that can be done is to isolate the section of the circuit that is creating the problem.

I would pull all the outlets and seperate the wires. You can megger at this point. If you find nothing One by one splice the circuits back. When the problem returns megger that run again. If nothing replace the section with a piece of fresh wire run exposed, try to emulate the approximate wire legnth that is in the wall.

If this does not work throw in the towel!
 

nizak

Senior Member
If you've already spent a ton of time on this I would get a 2 or 4 circuit inexpensive sub panel (HOM, QO) wire it from the existing panel and try their style of AF breaker. If it holds that would be a relatively inexpensive fix . I had a conventional breaker"phantom tripping" on me once it ended up being some expanding spray foam had penetrated a metal outlet box and their was a slight nick in the hot conductor at the box clamp. When certain movement occured in a particular room it would push against the conductor, short out, it would clear itself after resetting but would then re trip(sometimes a week later) when it would touch again for whatever reason.
 

kbsparky

Senior Member
Location
Delmarva, USA
Do they have any power strips with surge protection built-in? Those things can shunt surges to ground, causing AFI and GFI devices to think there is a ground-fault condition ....
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
How about dimmers, Are there any dimmers and other motor loads that could be causing this.
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
Did anybody ask if this was the actual AHJ's daughter? Does OP have only one guy in his area that's the authority on the electrical work performed in the jurisdiction? Seems kind of dangerous to me.
 