richwaskowitz
Senior Member
- Location
- Shelby Twp. MI, near Detroit
We had a sustained after hours brownout here a few months after I installed a Generac 20 kW with automatic xfer switch and the voltage was somewhere around 85/170 volts (out of 120/240). The xfer switch never dropped out and we lost an AC unit, a UPS and our mail server so I really got called onto the carpet by the IT dept. I went back and read the Generac docs and saw that it is set to drop out at 65% (78/156) !!! Isn't that crazy? I would have expected it to be much more sensitive than that or at least configurable. Now I need to add external undervoltage detection so that this never happens again. Have you seen this too?