PVC expansion joints on other than straight runs?

Status
Not open for further replies.

Electron_Sam78

Senior Member
Location
Palm Bay, FL
I know when using PVC we must use expansion couplings to account for expansion and contraction of the conduit on straight runs between fixed equipment. But what happens on long runs with 90s or large offsets at each end before entering equipment?
 

jaylectricity

Senior Member
Location
Massachusetts
Occupation
licensed journeyman electrician
Support clips after a bend count as fixed.

It's pretty simple, just imagine if the pipe got longer or shorter; would it put additional stress on the pipe at certain support points?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Good question on the offsets. IMO you would still need an expansion fitting if the expansion exceeded the dimension in 352.44. For what it's worth an offset would consist of two elbows even if they were less than 90?.
 