High Impedance Grounded Neutral

Status
Not open for further replies.

pete m.

Senior Member
Location
Ohio
Looking at the informational note following 250.36(C).

There it states: "The impedance is normally selected to limit the ground-fault current to a value slightly greater than or equal to the capacitive charging current of the system."

Is there a way to calculate this value or is it a value that can only be determined by taking readings?

Pete
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
There a several 'rules of thumb' used to estimate charging current.
The large HRG manufacturs, like Post-Glover and I-Gard, have technical papers dealing with this topic.
 