Tranformer OCP and conductor sizing

Status
Not open for further replies.
The NEC Code is new ground for me. I?ve followed the example for the 45kVA transformer in the following link: http://www.mikeholt.com/mojonewsarchive/NEC-HTML/HTML/TransformerInstallation~20020516.htm.

I have a contractor that insists that my OCP and conductor sizes are too high because transformers are only good for 80%. I do not see any guidelines in NEC or on the internet for derating transformers. Any comments on this would be appreciated.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I have a contractor that insists that my OCP and conductor sizes are too high because transformers are only good for 80%.
Your contractor is wrong.

There is no basis in the NEC for sizing protective devices based on anything other than 100% of the transformer nominal rating.
When someone says 'it is code' ask for a reference.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Your link is a good article from Mike Holt. Whoever is giving you this 80% information is incorrect.

Welcome to the Forum. :)
 