Guyute
Member
- Location
- Ft Collins, CO
I have a 400amp service with a main breaker and two 42 space panels. Main breaker, feed thru lugs, and a second 42 space panel. I have paralle runs of #300al and am confused about the sizing of the supply side equipment bonding conductor. If I am reading 250.102 C (2) with paralle runs I would need 1/0 for bonding the cans, bond bushings, etc. Is this the correct sizing from table 250.66 or should I be using the 3/0al based on the 400amp 700al needed for a single run. Thanks