Quick question, do I need a gfci on the roof of a commercial building? The receptacle will just be general use.
Thank you
Joe
Thank you
Joe
Quick question, do I need a gfci on the roof of a commercial building? The receptacle will just be general use.
Thank you
Joe
If you put a receptacle on the roof, it needs to be GFCI, and WR, and with a WR in-use cover.
I agree with the replies sofar, however I might add if receptacle required because of some equipments needing service / maint. then receptacles must be placed not more than 25ft from closest edge of any equipment enclosure.