The voltage in the J-box is 24vac. The box is a Type 4. Are seal-offs required at the box?
J jc3l Member Jan 24, 2012 #1 The voltage in the J-box is 24vac. The box is a Type 4. Are seal-offs required at the box?
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Jan 24, 2012 #2 Seals are only necessary when the box is required to be explosionproof. See 501.15(B)(1).
J jc3l Member Jan 26, 2012 #3 In this case should the j-box be rated xp? Low voltage with no arch producing devices inside. Thanks for your help.
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Jan 26, 2012 #4 Probably not; but see 501.10(B)(4) just in case.