Our factory has recently made a decision to have all the communication and phone lines that drop from the ceiling, (in open air), to be "ty-rap" attached to the nearby 110v power drops, (buss drop cable). I don't believe this is allowed. What about the 2" separation? Any thoughts?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
300.11(C) prohibits cables to be used to support other cables, raceways or other nonelectrical equipment.

Also the 2" separation is for conductors not cables.

Chris
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Power poles have a solid divider to separate the line and low voltage.

Dividers are not necessary if listed cables for line voltage and communications (example- MC and CAT5) are being used. If the line voltage were separate THHN conductors then a divider must be used between them and the communications cables such as CAT5.

Also, you can't run flexible cordage in conduit or raceway which I believe a power pole would constitute.

You could use a length of strut from the ceiling as a support and ty-rap everything to that.

-Hal
 
"Ty-rap" straps are not really being used as a means of supporting the communication cables, but rather a means of keeping the drops attractive and not hanging all over the place. Im not sure that it is truly a means of support. Both the communication cables and the 110v power drops are supported individually from the ceiling.
 

kwired

Electron manager
Location
NE Nebraska
"Ty-rap" straps are not really being used as a means of supporting the communication cables, but rather a means of keeping the drops attractive and not hanging all over the place. Im not sure that it is truly a means of support. Both the communication cables and the 110v power drops are supported individually from the ceiling.

If it is holding it in a certain position why is it not support?
 