I am installing power for Hot Tubs that will be on display and filled with water in an indoor retail showroom. There is the possibility of a customer getting in and trying out the spa once and a while. They are 240/120 volt 60 amp. They do not give you actual load just 60 amp circuit required. Because the spas are constantly being moved and changed out for different models, we would like to use a 6/4 SO cord to a 60 amp 3R receptacle enclosure. The cord would not be fastened to the structure and be about 25 ft long to allow for different scenerios. The outlet of course would be on a GFCI breaker. I realize this is not an approved wiring method for an indoor installation but is there any exception that would allow this for display purposes. What about 400.7 (6) utilization equipment permitted for frequent change?
I sized the cord for 55 amp 400.5(A) column B based on the fact that the spa, worst case would pull 80% of the 60 amp that the manufacturer rate it at. (125 % of 48 amp = 60 amp)
Any thoughts?
I sized the cord for 55 amp 400.5(A) column B based on the fact that the spa, worst case would pull 80% of the 60 amp that the manufacturer rate it at. (125 % of 48 amp = 60 amp)
Any thoughts?