- Windsor, CO NEC: 2017
- Service Manager
This proposal would force all service disconnects to be mounted outside.
1.) Comment on Proposal No.: 4-144
2.) Recommendation: Accept the proposal.
3.) Substantiation: To rebut each of the panel's ostensibly contrived statements:
1. All service disconnects I have seen have a means for locking the disconnect closed with a padlock, which is permissible by code. To claim that there is a security risk involved is misleading. Security and communication equipment often have means for continued use after power loss; security systems have battery backup, and POTS does not require local power to operate.
2. An exception can be added if the panel feels that inner city environments would be adversely affected by this change.
3. An exception can be added for services over 1000V.
4. Data was presented to the panel in the last code cycle (Proposal 4-132 2010 ROP) detailing two separate incidents which resulted in property damage explicitly because the service disconnects were allowed inside. It was remarkable in both incidents that there were no loss of life.
5. In the cases mentioned in item #4 above, no covers were removed by unqualified personnel - but covers were removed by arc blasts that could have claimed the lives of several people.
6. 240.24(D) already prohibits overcurrent devices from installation in corrosive environments, and this section does nothing to add to that concept.
Billions will be spent on AFCI breakers that may or may not make an impact on electrical safety. This proposal has no appreciable cost impact yet would make an indelible difference in safety to both workers and occupants. The panel should reconsider it's decision.
Panel Statement on 4-144 said:A main outdoor disconnect also creates a security issue where criminals could interrupt service to defeat security and communication equipment. A requirement to install a disconnect outside with the meter would present difficulties in inner-city environments where underground service conductors enter a building from underground distribution systems. The meters are in the basement, or in recessed enclosures on the front wall of the building. There is limited space on building walls in row home neighborhoods to add a main switch ahead of the meter. This would also present difficulties for facilities served at voltages over 1,000 Volts. The submitter has not presented any technical data to support such a change. Unqualified persons should never remove electric meters nor should they intentionally expose themselves to electrical hazards. Overcurrent devices installed outdoors where they are subject to corrosive environments many times fail or become inoperable for emergency situations.