brigadier_92
Member
Greetings to all:
A question has come up in reference to the fire pumps installed at a high rise building 30 floors
Background:
Each of three pumps is controlled via its own UL approved fire pump controller.
The building is presently equipped with three fire pumps as follows:
200 HP diesel fire pump with its own dedicated fuel source. This pump serves the upper floors.
200HP electric fire pump connected via a separate utility service feeder with a 600AMP fused disconnect. The fire pump controller is a primary resistor reduced voltage type. This pump serves the upper floors as an alternate.
60HP electric fire pump with connected via the same 600 AMP fused disconnect. The fire pump controller is a primary resistor reduced voltage type. This pump serves the lower floors of the building.
Both of the electric fire pumps are also connected to the building?s emergency generators via a 600 AMP automatic transfer switch.
The fire pump controller for the 200HP electric requires replacement as parts are no longer available for its maintenance.
As a result of the replacement of the fire pump controller, an electrical contractor is alleging that the current installation does not comply with the provision requiring the electrical service disconnecting means to be able to carry the locked rotor currents of the motors indefinitely.
In the case of the 200 HP motor, the amounts to 1450 AMPS. Our present utility service disconnecting means is 600 AMPS.
And now, our question. Does the fact that the building is equipped with a diesel fire pump, in any way allow for the alternate pump with two sources of available energy mitigate the apparent requirement for such a large electrical service disconnecting means and larger service capacity?
Thoughts?
A question has come up in reference to the fire pumps installed at a high rise building 30 floors
Background:
Each of three pumps is controlled via its own UL approved fire pump controller.
The building is presently equipped with three fire pumps as follows:
200 HP diesel fire pump with its own dedicated fuel source. This pump serves the upper floors.
200HP electric fire pump connected via a separate utility service feeder with a 600AMP fused disconnect. The fire pump controller is a primary resistor reduced voltage type. This pump serves the upper floors as an alternate.
60HP electric fire pump with connected via the same 600 AMP fused disconnect. The fire pump controller is a primary resistor reduced voltage type. This pump serves the lower floors of the building.
Both of the electric fire pumps are also connected to the building?s emergency generators via a 600 AMP automatic transfer switch.
The fire pump controller for the 200HP electric requires replacement as parts are no longer available for its maintenance.
As a result of the replacement of the fire pump controller, an electrical contractor is alleging that the current installation does not comply with the provision requiring the electrical service disconnecting means to be able to carry the locked rotor currents of the motors indefinitely.
In the case of the 200 HP motor, the amounts to 1450 AMPS. Our present utility service disconnecting means is 600 AMPS.
And now, our question. Does the fact that the building is equipped with a diesel fire pump, in any way allow for the alternate pump with two sources of available energy mitigate the apparent requirement for such a large electrical service disconnecting means and larger service capacity?
Thoughts?