Ok I have read all the threads on 310.15 b 6. But none really apply to my question.
Have a 200 amp pedestal that feeds the house with 100 amp breaker, also feeds from pedestal a shop with 40 amps.
Owner wants to be able to hook a generator up when power goes out, only to the house which is 100 amp. this will be thru a manuel 100 amp transfer switch.
Can I use #4 to the x-fer switch then back to the house? Or is this (the house panel) a sub panel and have to use #3? I read as a sub panel.
Pedestal is away from house. And tried to see what is feeding it now but can't tell.
I have seen 100 amp meter panel on pole to feed mobile home. Underground to 100 amp panel in mobile home feed with #4, I think it should be #3, but they pass everytime. Am I wrong?
Thanks for any help.