Is there an NEC code requirement to keep a certain amount of separation between electrical lines and gas lines in the same trench?
 
Gas\Electrical separation

Gas\Electrical separation

Thanks for your help. I didn't think there was, but I wanted to check in with the experts!
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
The NESC has a section (353), deliberate separations. There is a rule for utilities, (Gas, communication, and electric) but as the others have stated, not in the NEC.
 