Some customers are picky about our terminations and will not accept die-less crimps on current-carrying connections. We are the same folks who specify two-hole lugs and long barrel compression lugs on current-carrying connections. We require compression lugs for grounding/bonding connections, but we do not require long barrel lugs or two hole lugs and we permit die-less crimpers to be used on grounding/bonding connections.
Before someone points it out, yes we know that ground/bonding is critical to clearing faults and shouldn't be neglected. The failure modes that we're trying to mitigate through the use of two hole bolted connections, long barrel lugs, and die type crimpers are all thermal failure modes that develop over time - in other words the failure is caused by many months or years of significant current flow through the connection. Grounding/bonding lugs see very short, occasional current flow and hence don't require some of the same design features since the same failure modes are not present.