I have (6) 1.25MVA generators feeding a paralleling switchgear. .... calculate the short circuit of each individual generator and multiply by (6) generators? Or do I consider the system as (1) 7.5MVA generator with an equivalent parallel Xd" (1/Xd" total = 1/Xd"1 + 1/Xd"2 + ...)?
Calculate for one generator and multiply by 6.
I short circuit = FLA/Xd" = [1.25 x 1000/(.480 x 1.732) ] /0.2 = 1504 /0.2 A = 7517 Amps per generator.
7517 Amps x 6 = 45,106 Amps
Or using the MVA method:
Assume typical Xd" = 0.2, Short Circuit MVAsc = 1.25 MVA/ 0.2 = 6.25 MVA,
I short circuit = MVAsc x 1000 / (kV x1.732) = 7517 amps (assuming 480 V).
Total short circuit = 7517 amps x 6 = 45,106 Amps.
Same answer if we multiply MVAsc of one generator by 6 and calculate amps.
6.25 x 6 = 37.5 MVA total short circuit power,
I = 37.5x 1000/(0.480 x 1.732) = 45,107 Amps.
Since the impedance Xd" is per unit or per cent and not in actual ohms we don't need to calculate the parallel impedance. Example:
Six each 1.25 MVA units = 7.5 MVA all with Xd"=0.2. MVAsc = 7.5/0.2 = 37.5 MVA, same answer as above.