At a hospital I do alot of work for, they've recently lost their backup generator. Not their only generator but the one that backs up the Level 1 Emergecy Generator. Since they deem this backup of the backup as essential, they've gone out and gotten a temp unit. THe temp unit is a 500kW. THe existing unit is a 350KW.
There are some obstacles to replacing the dead generator, they're going to live with this arrangement for the next, maybe 6 months but they're having a strange problem. When they last tested the temp and permanent generator they simulated the stationary generator dying and switched over to the temp. All went according to plan - no problem. So then they switch back to the existing generator and circuit down stream breakers tripped. a 100A-3P was the largest but also a 50A-3P and several 20A-1P. I've not yet investigated to find out exactly which breakers these are but I'm told they're all fairly down stream in the distribution.
The question is what could possibly be causing this to happen. If you switch from utility to the 350kW generator nothing happens. Why would these breakers be tripping when they switch from the temp generator to the old. All transitions by the way are open transitions.
Any thoughts
There are some obstacles to replacing the dead generator, they're going to live with this arrangement for the next, maybe 6 months but they're having a strange problem. When they last tested the temp and permanent generator they simulated the stationary generator dying and switched over to the temp. All went according to plan - no problem. So then they switch back to the existing generator and circuit down stream breakers tripped. a 100A-3P was the largest but also a 50A-3P and several 20A-1P. I've not yet investigated to find out exactly which breakers these are but I'm told they're all fairly down stream in the distribution.
The question is what could possibly be causing this to happen. If you switch from utility to the 350kW generator nothing happens. Why would these breakers be tripping when they switch from the temp generator to the old. All transitions by the way are open transitions.
Any thoughts