Spend the money on a pin & sleeve. Or, even spring for an interlocked receptacle and switch, where the plug can not be removed unless switch is off.This is a self contained chop saw on a rolling platform to be able to roll to the wire rope cable. It will need to be able to be wired so as to move it to other locations of the facility. I am open for suggestions
This is a self contained chop saw on a rolling platform to be able to roll to the wire rope cable. It will need to be able to be wired so as to move it to other locations of the facility. I am open for suggestions
Does anyone know of a receptacle and cord cap that is rated 60A ,20HP 3 phase other than a pin and sleeve receptacle, that would be a little more cost effective for connecting a chop saw.
I cannot imagine unpluging a 20HP motor while it is running.
I think I will put a Disconnect ahead of the pin an sleeve. Thanks everyone for all your inputs
This is just a belt drive abrasive saw, isn't it?They are fairly low inertia. Move it over by the panel and try it. If it holds for the start it should be ok during cutting.The code doesn't specify a min size on the breaker does it? Is this your shop, isn't it?Had another question on the size of the breaker for a 20hp at nameplate amps of 46A at 240V.
Using table amps at 54A x 250%= 135A. I can only use a 100A breaker because of the load center can only accept a max of 100A breakers. Do you all think a 100A breaker would be suffient for this application.
No this is not my shop. Yes this is a belt driven saw. Its a customer of mind. I just want to be able to let them know the circumstances with the start up of this saw, and the system they have. I feel like they should of purchased a 10HP saw. They purchased without asking if the facility could handle this 20Hp. It can handle it if a 100A breaker will allow start up.