Fuel Tank Classification

Status
Not open for further replies.

session88

Member
Location
USA
We have a outdoor diesel tank used to dispense fuel to equipment. It is next to a massive hill/mound of coal. The tank and all associated fittings are constantly covered in a layer of coal dust.

Question is: What exactly is this Hazardous (Classified) Location?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Based solely on your description, it is most likely Class II, Division 2, Group F. Without seeing the installation, I have no idea what the boundaries are or if there are potential Class II, Division 1 locations. The "T-rating" is also questionable without knowing more specifics about the coal.
 