NM vs UF into back of an exterior box on exterior masonry wall

  • NM may be used without sleeving

    Votes: 2 10.5%
  • NM with a sleeve thru the masoinry

    Votes: 0 0.0%
  • UF or a conduit with THWN

    Votes: 2 10.5%
  • 1, 2 or 3 are all acceptable

    Votes: 12 63.2%
  • 2 and 3 are acceptable

    Votes: 3 15.8%

  • Total voters
    19
  • Poll closed .
Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In another thread the OP advised he was required to use UF (or a method other than NM) to enter the back of a box mounted on the extrior of a block wall.
What method is allowed in your area ?
 

resistance

Senior Member
Location
WA
We can talk all day about rather an area inside a piece of electrical equipment can be wet or damp. The fact of the matter is, it can be both, depending on the ambient temperature, or conditions. But, based on code, the installation of #1-3 is fine?depending on your jurisdictional code.
 