I have a new generator installation, 150 kW 208V 3-phase on a concrete pad. The generator will come equipped with (2) 400A breakers to feed (2) electrical panels (with MLO terminals) in the building via (2) 400A Automatic Transfer switches. The ATS's will switch the neutral making this a seperately derived system. My plan is to install (4) 500 kcmil copper conductors between the ATS and the 400 amp breaker for each panel with NO equipment grounding conductors. The 500 kcmil is rated at 380 amps, 75 degree column of 310.15(B). I will install a main bonding jumper in the generator based on the (2) parallel feeds, or 1000 kcmil and use a 2/0 copper conductor based on 250.66. I will also connect a 2/0 copper to building steel and supplement this with a #6 copper to a ground rod. In my opinion the ground rod is not required, but the generator manual states the installation should have one. Finally, here is my question: Does 445.13 apply when you have OCPD's at the generator? Should i install 600 kcmil to carry the full 400 amps? If wondering, the calculated load on each panel is in the low 200's as the generator was sized for future expansion.
Thanks,
Mike
Thanks,
Mike