Someone asked me today about re-identification of ungrounded conductor #6 and smaller and i replied that it can be done and there is no code article disallowing it.
I just want to confirm that the smaller than #6 (other than white & EGC) can be re-identified.
Thanks.
resistance
WA
That is not true. An ungrounded conductor can not be re-identified to indicate that it’s a grounded, or equipment grounding conductor—if the ungrounded conductor is smaller than #6. Yet, you can change the color of an ungrounded conductor to any color other than white, gray, or green (If smaller than #6). See NEC 200.6 and 250.119.
resistance
WA
I’m basing my answer on what the OP said. Which was:
To me, it seems the OP is saying an ungrounded conductor can be re-indentified to any color—if the conductor is smaller than #6. Then the OP says, “do not include the grounded and EG conductors smaller than #6”. As the OP knows that these conductors can not be re-identified.
Ponchik
CA
Electronologist
That is not true. An ungrounded conductor can not be re-identified to indicate that it?s a grounded, or equipment grounding conductor
i agree.
I was just confirming the ungrounded (colored other than white or green) conductor to be re-identified to another ungrounded conductor.
Thanks for the confirmation.
bknight
New member
Dallas, TX
Smaller than # 6.....
Similar question:
Acoording to 200.6 a wire smaller than a # 4 ( say a black #8) can not simply be marked white at the terminal ends...correct? Where does 200.7 play into this equation? This seems to be very confusing to me.
Thanks for the help.